H3C R6900 G5. RAM dimm error = 8pcs

2023-03-26 19:16:38 Published
  • 0 Followed
  • 0Collected ,1430Browsed

Network Topology

irrelevant

Problem Description

Device H3C UniServer R6900 G5 Chassis

The RAM dimm are not working (8pcs in total, according customer request) on 2023.03

Process Analysis

According to the log, some alarms were generated in 2022.10. 

No MCA error, so first check that the installation is correct.

 


125

 Warning

NA

NA

NA

From BIOS

2022-10-09 04:17:02

ENGINEER

Ewl type 0x1---, SeverityLevel: warning, Size: 0x12, MajorCheckpoint: 0xb7, MinorCheckpoint: 0x12, MajorCode: 0x19, MinorCode: 0x1, Socket: 0x0, Channel: 0x0, Dimm: 0xff, Rank: 0xff

126

 Warning

NA

NA

NA

From BIOS

2022-10-09 04:17:02

ENGINEER

Ewl type 0x1---, SeverityLevel: warning, Size: 0x12, MajorCheckpoint: 0xb7, MinorCheckpoint: 0x12, MajorCode: 0x19, MinorCode: 0x1, Socket: 0x0, Channel: 0x1, Dimm: 0xff, Rank: 0xff

 

Solution

1.Remove and reinsert these 8 faulty memory and clean the goldfinger, issue resolved

2.So tell customer that  please pay attention to the server environment such as the dust.

 Temperature and humidity requirements

To ensure correct operation of the server, make sure the room temperature and humidity meet the requirements as described in "Appendix A  Server specifications."

Equipment room height requirements

To ensure correct operation of the server, make sure the equipment room height meets the requirements as described in "Appendix A  Server specifications."

Cleanliness requirements

Mechanically active substances buildup on the chassis might result in electrostatic adsorption, which causes poor contact of metal components and contact points. In the worst case, electrostatic adsorption can cause communication failure.

Table 3 Mechanically active substance concentration limit in the equipment room

Substance

Particle diameter

Concentration limit

Dust particles

≥ 5 µm

≤ 3 x 104 particles/m3

(No visible dust on desk in three days)

Dust (suspension)

≤ 75 µm

≤ 0.2 mg/m3

Dust (sedimentation)

75 µm to 150 µm

≤ 1.5 mg/(m2h)

Sand

≥ 150 µm

≤ 30 mg/m3

 

The equipment room must also meet limits on salts, acids, and sulfides to eliminate corrosion and premature aging of components, as shown in Table 4.

Table 4 Harmful gas limits in an equipment room

Gas

Maximum concentration (mg/m3)

SO2

0.2

H2S

0.006

NO2

0.04

NH3

0.05

Cl2

0.01


Please rate this case:   